There may still be a grey area as to whether they constitute an Appliance under NEC
If they do meet that criterion, then you may have to run a web of strings connecting breakers in different panels or something equally absurd to meet the grouped disconnect criterion.
I suppose if the entire aisle or row is considered one "appliance" then you could group the disconnects by having one motor panel, one lighting panel, etc. for each aisle placed compactly together and call it a grouping.
But once you put several aisles on one panel, the grouping becomes pretty tricky.
PS: The more I think about it, the more I would say that an individual case section would not be an appliance, but the whole aisle might be.... Or at least the whole part of the aisle that shares the same air space inside the doors.
440.3 Other Articles. (A) Article 430. These provisions are in addition to, or amendatory of, the provisions of Article 430 and other articles in this Code, which apply except as modified in this article.
(B) Articles 422, 424, or 430. The rules of Articles 422, 424, or 430, as applicable, shall apply to air-conditioning and refrigerating equipment that does not incorporate a hermetic refrigerant motor-compressor. This equipment includes devices that employ refrigeration compressors driven by conventional motors, furnaces with air-conditioning evaporator coils installed, fan-coil units, remote forced air-cooled condensers, remote commercial refrigerators, and so forth.
422.1 Scope. This article covers electrical appliances used in any occupancy.