Re: Supplemental rod required even with 9 Ohms Resistance?
Originally posted by sfav8r:
Interesting replies. Thank you.
I requested a meeting with the head honcho (first time in 11 years). I'll let you know how it goes.
Thanks again for the input.
Well, the meeting was informative...in a very frustrating sort of way. The bottom line is this:
AS we all previously discussed, 250.56 sets the standard at 25 ohms. The San Francisco Amendments do not address or alter this section, so it is exactly the same as the NEC.
At some point, the question was raised by one or more inspectors, "well, how do we verify the ground rod resistance?"
The city had several options to choose from.
1) Trust the EC to test and properly report the resistance.
2) Provide a means of testing for all of the inspectors.
3) Make it mandatory to have a 3rd party verification an all installations.
4) Require EITHER 2 rods or a 3rd party verification.
SF opted as a POLICY to initiate option four. I concede that they have a legitimate concern here. I do have two problems with their answer though.
First, there is absolutely no reason that the "Policy" cannot be adjusted to allow for demonstration of 25 ohms or less by the EC at the time of inspection. They could require that the meter be up and ready to demonstrate at the time of inspection. In the case of my meter this takes about 15 seconds.
The meter comes with a test grid that you clamp onto and is marked off in ohms (.0472 ohms, 10 ohms, 47.2 ohms, and 100 ohms), therefore, one can easily verify proper operation very quickly.
The BIG problem I have, is that there is no effort by the city to publish the policy and distribute it to ECs in the area so they'll know what to expect. Let me restate that more accurately...There is no effort by the city to distribute this information to non-union contractors. It turns out that the city does send this information to the local union so they can inform their guys ahead of time!
I questioned (with all the diplomacy I could muster) the equity in this. The city's position is that the union is a single point of contact for a number of contractors and it is a very efficient way of getting the word out.
I suggested that their web site would be an efficient way to distribute this information and offers the advantage of informing ANY interested contractors, not just the union guys. He agreed, but didn't even know if the information is there or if there were plans to put it there.
On the upside, when I mentioned that SF is still on the 99 NEC and this is 2005 and I have never had this problem before he gave me the most honest answer I have ever received from the city. "A lot of our inspectors think its BS and they just don't bother with it."
I requested and received a copy of the district map where the original inspector works. I will still bid jobs there but will adjust my bids with the knowledge that I can count on at least two inspections, 2 ground rods, the gas pipe cannot be bonded at the hot water heater, plastic cover plates are not acceptable in the garage if it is not sheet rocked...