Thank you for the welcome to the forum and helpful responses, this is most appreciated.
Here's some answers to the questions and more information.
The equipment only requires 240V, ie no neutral required. The 240V supply goes to a number of switch mode supplies and whilst these will run off 120V, we would need to increase the conductor sizes which is not practical, hence using 240V is preferred and very close to 230V in Australia (in practice usually 240V). The equipment current at 240V is <10A so quite modest,
The equipment is earthed so we would require L1, L2 and Earth but no Neutral. We are reluctant to use the IEC Brown, Blue and Green/Yellow cable as Blue is associated with Neutral and this would be connected to L1/L2. As I understand it, the NEC does not prescribe colours for L1, L2 (Hot), but it would seem better practice to use Red, Black and Green/Yellow rather than the IEC colours is this correct?
For the wall connection what plug/socket is used, would this be NEMA 6-20?