ivsenroute
Senior Member
- Location
- Florida
I was at a local supply house and a gentleman was at the counter. He had apparently asked what he needed to hook up his hot tub so the salesman gave him a 50A GFCI Spa Disco and some 10/2 UF.
Another counter person saw the transaction and told the customer to wait becuase he was given the wrong size wire. He went into the back and came out with 8/2 UF and said "here you go, now you are good for 50Amps".
I just kept quiet since it was none of my business.
How often do you see this?
I questioned the salesman the next day and said for UF he should have been given 6awg copper, not 8. He told me that they always give out 8 copper for NM and UF wire when the OCPD is 50A.
Does your supply house have an NEC handy?