M msi99 Member Location Texas Occupation Solar Jan 20, 2023 #1 If the property already has an existing enphase system hooked up as a line side, can we add a solar edge system to the property via a back feed if the 120% rule is satisfied?
G ggunn PE (Electrical), NABCEP certified Location Austin, TX, USA Occupation Consulting Electrical Engineer - Photovoltaic Systems Jan 20, 2023 #2 Sure, if the AHJ is OK with two points of interconnection on the service. The supply side connection did not change anything in the panel.
J jaggedben Senior Member Location Northern California Occupation Solar and Energy Storage Installer Jan 20, 2023 #3 The only other thing is that the combined output of the systems can't exceed the service rating. Which is probably unlikely anyway.
G ggunn PE (Electrical), NABCEP certified Location Austin, TX, USA Occupation Consulting Electrical Engineer - Photovoltaic Systems Jan 20, 2023 #4 jaggedben said: The only other thing is that the combined output of the systems can't exceed the service rating. Which is probably unlikely anyway. Click to expand... Right; I didn't think of that but as you say, for residences the PV output not very likely to approach that limit.