I have a few questions about supply-side connections.
1) Are only fused disconnects allowed or can a breaker be installed as the first over-current protection after the supply-side connection, as long as the breaker panel/bus is rated for greater than 60 A per 230.79(D) and it is service rated & lockable per utility requirements.
Example, 6 inverter outputs are combined in an AC panel with a 200 A main breaker. If this "AC combiner" panel is service rated, lockable and grouped with the main service disconnect can the 200 A main breaker be used as the first over-current protection for the supply-side connected conductors or would an additional fused disconnect be required?
2) Grounding & bonding conductor sizing gets fuzzy between the main solar disconnect and the supply side connection. As I understand it the grounded conductor should be bonded to the pv disconnect per 250.24, i.e. the neutral is connected to ground. Am I sizing the bonding jumper to 250.66?
In a residential scenario where i am connecting to conductors inside a main service panel on the supply side of the breaker can I skip bonding the inverter neutral to ground in the PV disconnect and just land my ground on the appropriate terminals in the main service panel as the neutral bus is bonded to the ground bus at the main panel/service?
Would I still size the ground wire/egc between the PV disconnect/OCPD and the supply connection to 250.66?
Clarification is much appreciated.