I am seeking input regarding a proposed 18 kW single phase system that I would like to tie in to an existing 200A single phase service.
I will start by saying that my experience with supply side connections is limited.
I will be approaching an electrical engineer with this scenario, but would like to have an understanding of the pros and cons.
The utility enters a Milbank meter mains enclosure with a 200A breaker on a pole roughly 50' from the building. From there, the conductors run to an interior 200A load center with 200A breaker.
The output of two inverters will be combined and have a continuous output of 75A and require 100A of overcurrent protection.
I understand that I have two options:
Run conduit to the outdoor meter mains and tap into the service between the meter and the main breaker. (Is the 1' of wire between meter and main breaker enough to make a tap?)
or
Upgrade the 200A meter mains to a 300A and make a load side connection between the meter mains main breaker and the interior load center.
Your input is appreciated.
I will start by saying that my experience with supply side connections is limited.
I will be approaching an electrical engineer with this scenario, but would like to have an understanding of the pros and cons.
The utility enters a Milbank meter mains enclosure with a 200A breaker on a pole roughly 50' from the building. From there, the conductors run to an interior 200A load center with 200A breaker.
The output of two inverters will be combined and have a continuous output of 75A and require 100A of overcurrent protection.
I understand that I have two options:
Run conduit to the outdoor meter mains and tap into the service between the meter and the main breaker. (Is the 1' of wire between meter and main breaker enough to make a tap?)
or
Upgrade the 200A meter mains to a 300A and make a load side connection between the meter mains main breaker and the interior load center.
Your input is appreciated.