ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
I realize you are aware of that for your particular installation. What I'm saying is the Code is written from the perspective of not knowing. What if the main bonding jumper at the service disconnect, sized to its tap conductors, is smaller than your [so-called] EGC?
It's never going to happen. We are limited to the size of the service with a supply side interconnected PV system.
Still reading the rest of your response...