What are the other bonding jumpers from that table? Are they typically before or after an OCPD?Is it safe to say that all other bonding jumpers are on the load side even though they also sized to t.250.102c
What are the other bonding jumpers from that table? Are they i was asking because they are on the same table
Take a look at 250.102(D)Yes they are I was asking because I wanted to know why are they all on the same table
Thank you but that doesn’t answer my questionTake a look at 250.102(D)
Sure it does...It tells you to use Table 250.122 and not 250.102 when the bonding jumper is on the load side of an OCPD.Thank you but that doesn’t answer my question
TySure it does...It tells you to use Table 250.122 and not 250.102 when the bonding jumper is on the load side of an OCPD.