I was failed on an above ceiling inspection because I supported mc cable on the ceiling grid wire
300.11.2 Exception allows this in a non fire rated ceiling as long as it is installed per the manufacture's instructions.
Here's the tricky part...According to the manufacture they do not have instructions for installing lighting whips. As long as the lighting whips do not interfere with the grid being level and square and the cable is not resting on the grid the manufacture has no interest in how you install or support them. They defer to ASTM 636c which only stats you can not bend the grid wire to level the ceiling when installing the ceiling grid.
The inspector wants individual wire supports hung from the structure and tied off to the grid to support the MC cable. I dont believe I need to do that
300.11 is vague, 300.11.2 is very clear as is the exception...Any thoughts would be appreciated
300.11.2 Exception allows this in a non fire rated ceiling as long as it is installed per the manufacture's instructions.
Here's the tricky part...According to the manufacture they do not have instructions for installing lighting whips. As long as the lighting whips do not interfere with the grid being level and square and the cable is not resting on the grid the manufacture has no interest in how you install or support them. They defer to ASTM 636c which only stats you can not bend the grid wire to level the ceiling when installing the ceiling grid.
The inspector wants individual wire supports hung from the structure and tied off to the grid to support the MC cable. I dont believe I need to do that
300.11 is vague, 300.11.2 is very clear as is the exception...Any thoughts would be appreciated