ericmccurley
Member
- Location
- Arkansas
- Occupation
- Electrician
I got a new electrical job in a small town. This little house has been abandoned for a few years and is not up to electrical code. There are not enough electrical outlets throughout the home is there anywhere in the code that states I cannot simply cut in a outlet and run the Romax from the attic straight down to the outlet without removing the sheet rock on the wall? Yeah it the Romax will not be supported by staples in the wall but I’ve done this plenty of times for homeowners that want a few receptacles added in the home they’re living in.