SureTest 61-157

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I have a 61-155 and have been happy with it and have been thinking about a 61-157 for some very basic THD testing, (company can supply recorders or scopes)
does anyone here have experience with this analyzer, and if so what do you think?

Roger
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: SureTest 61-157

Roger, I have one along with the 61-181 clamp-on probe. I have been extremely happy with mine. Only thing that threw me at first was plugging into a GFCI, it will trip it. It is due to the fact the unit puts a load from L-G to read the ground impedance. Reset the breaker and evrything OK from there on.

Its a snap to determine if there are ant N-G on the circuit, you can determine the load of about any device, yadda, yadda, yadda. Buy it, you will like it. Easy to operate, one button.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: SureTest 61-157

Dereck, thanks for the reply, thats all I needed to make up my mind. I had planned on going ahead and buying the 61-181 too. Thanks again.

Roger
 