SureTest 61-157

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I have a 61-155 and have been happy with it and have been thinking about a 61-157 for some very basic THD testing, (company can supply recorders or scopes)
does anyone here have experience with this analyzer, and if so what do you think?

Roger
 
Re: SureTest 61-157

Roger, I have one along with the 61-181 clamp-on probe. I have been extremely happy with mine. Only thing that threw me at first was plugging into a GFCI, it will trip it. It is due to the fact the unit puts a load from L-G to read the ground impedance. Reset the breaker and evrything OK from there on.

Its a snap to determine if there are ant N-G on the circuit, you can determine the load of about any device, yadda, yadda, yadda. Buy it, you will like it. Easy to operate, one button.
 
Re: SureTest 61-157

Dereck, thanks for the reply, thats all I needed to make up my mind. I had planned on going ahead and buying the 61-181 too. Thanks again.

Roger
 