- Location
- Tennessee NEC:2017
- Occupation
- Semi-Retired Electrician
Had a service call today for a supposed lightning strike. HO says a couple of breakers tripped and smoke was coming out of a wall switch. I get there and she has the breakers off. She said if she turns them back on that the smoke starts up again. I took the wall plate off that has visible scorch marks on it inside and out. This was a 2G box with a 3-way switch and a stacked switch. The stacked switch had a 3-way on the top half and single pole on the bottom. Both switches had burn/scorch marks. I checked both the 3-way and stacked switch and only the stacked switch showed bad.
This is strange to me because if it was a direct lightning hit I would think there would be more damage. If it was a surge, I would think it would have damaged the lights or bulbs as well. None of the insulation on the conductors appeared to be damaged, no scorch marks or any sign of them being hot. The HO was preparing for a trip and didn't have time for me to do an insulation test or much further investigation. I did check the panel and didn't see any visible damage there.
One of the switches was for the front porch light and she wanted it to be on while they were away. The other two switches worked a foyer light and upstairs hall can lights. So to give a quick test, I replaced the 3-way that had the burn marks as well as the other 3-way in another location. I didn't have a stacked switch that had a 3-way to replace hers, but I did have a stacked single pole switch. The 3-way portion of the stacked switch was part of a 4-way circuit. So I just tied one of the travelers to the light leg and capped off the other traveler. I used the other part of the stacked switch for her porch lights. I got all the lights back on and watched it for about 15 mins and saw no smoke nor tripping breakers. I told her to just keep an eye on it and leave just the porch lights on when they left for their trip.
Other than a Meg test, I don't know what else I could have done. Thoughts on whether this was a surge or direct hit? There were several storms here last night.
This is strange to me because if it was a direct lightning hit I would think there would be more damage. If it was a surge, I would think it would have damaged the lights or bulbs as well. None of the insulation on the conductors appeared to be damaged, no scorch marks or any sign of them being hot. The HO was preparing for a trip and didn't have time for me to do an insulation test or much further investigation. I did check the panel and didn't see any visible damage there.
One of the switches was for the front porch light and she wanted it to be on while they were away. The other two switches worked a foyer light and upstairs hall can lights. So to give a quick test, I replaced the 3-way that had the burn marks as well as the other 3-way in another location. I didn't have a stacked switch that had a 3-way to replace hers, but I did have a stacked single pole switch. The 3-way portion of the stacked switch was part of a 4-way circuit. So I just tied one of the travelers to the light leg and capped off the other traveler. I used the other part of the stacked switch for her porch lights. I got all the lights back on and watched it for about 15 mins and saw no smoke nor tripping breakers. I told her to just keep an eye on it and leave just the porch lights on when they left for their trip.
Other than a Meg test, I don't know what else I could have done. Thoughts on whether this was a surge or direct hit? There were several storms here last night.