Just completed an NFPA class in which they took the stance that a surge protection device is required at BOTH the MSP and any sub panel location. I expressed the opinion, based on 230.67, that a surge protection device at the main meets the minimum intent of protection. Is this incorrect? In places like California, we are required to prewire for battery back up/critical load panel in new SFD. So, based off their class, it would be required at the MSP, the critical load back up panel, and the other sub panel that is needed due to breaker space from the GFCI and AFCI requirements. Any feedback would be appreciated.