petersonra said:
I doubt the lack or presence of a ground on the X0 of the transformer will make any difference. It seems to me I read once that these things are deliberately not grounded for some reason. Did you check the manufacturer's literature? Did it have OCP on both legs of the secondary side of the transformer?
Normally it is not all that easy for a high frequency transient (AKA surge) to get through a transformer. Is it possible the transient is entering the controller from the low voltage side?
Do you see any blackened wires?
When you say fried what do you mean?
By fried I mean two of the relays on the board were burned.
OCP on one leg of secondary.
No blackened wires.
The transformer has no literature, it is about 10 years old, can't even read the nameplate.
It is possible the transient is coming from the low voltage side. It is operated by 4 floats (mecury switch type) and one of them is about 150' away.
It is a very old system very bad environment (sewer) all the wires were corroded so I cut of the ends and redone all of them. I also went ahead and put surge protection on both the 480 and 120.