hockeyoligist2
Senior Member
- Location
- close to greenville sc
We keep having a pump controller getting fried during storms. The controller is 120v from a transfomer located in the same box, 480 feed which supplies the transformer and the pump motors (submersible pumps). Nothing else gets blown out. IYO would surge protection be better on the 480 or the 120 or both? I did notice today when I replaced it (my first time replacing) that the secondary side out the transformer didn't have a connection to the ground so I installed one.