M makalroy1 Member Location WV Occupation Electrician Jul 8, 2025 #1 Can you suspend a 5ft piece of 1/2 rigid from a 4-11 box, mounted to the ceiling, to mount a 1lb LED light fixture? conduit is only supported by the box. Thanks
Can you suspend a 5ft piece of 1/2 rigid from a 4-11 box, mounted to the ceiling, to mount a 1lb LED light fixture? conduit is only supported by the box. Thanks
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jul 8, 2025 #2 I can't find an "official" answer but I would not be too concerned as the Steel City "SH" swivel hangers mount to a 4" box and are rated for 50 lbs.
I can't find an "official" answer but I would not be too concerned as the Steel City "SH" swivel hangers mount to a 4" box and are rated for 50 lbs.
S Strathead Senior Member Location Ocala, Florida, USA Occupation Electrician/Estimator/Project Manager/Superintendent Jul 8, 2025 #3 All day long.
M makalroy1 Member Location WV Occupation Electrician Jul 8, 2025 #4 Do I have to use a swivel hanger if longer than 18 inches
R retirede Senior Member Location Illinois Jul 8, 2025 #5 If the 1/2” rigid is also used as a raceway, isn’t it necessary to comply with support requirements?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jul 8, 2025 #6 makalroy1 said: Do I have to use a swivel hanger if longer than 18 inches Click to expand... I simply mentioned it as a validation for your plan.
makalroy1 said: Do I have to use a swivel hanger if longer than 18 inches Click to expand... I simply mentioned it as a validation for your plan.