Swimming Pool Bonding

Status
Not open for further replies.

eiplanner

Member
I am running into a lot of cunfusion with local electrical inspectors concerning swimming pool bonding. I would like to get an expert explanation for exactly what is required for the following specific application. Please quote articles, passages, training seminars or other methods of how your interpretation was developed.

Application:

Permanent inground, vinyl lined, metal wall swimming pool. (Metal walls consist of galvanized steel sections bolted together with zinc 3/8" bolts.)
One metal niche light fixture with factory installed bonding lug.

Interpretations:

Prior to the acceptance of the 2005 code, I would drill a 1/4" hole in the outer edge of a pool wall near the light niche, install a copper grounding lug to this hole with a 1/4" zinc screw, fasten the end of a #8 bare copper wire to this lug, run the wire through the lug on the light niche, and then run the wire back to the pool equipment. This was my interpretation of the code and always passed inspections.

After acceptance of the 2005 code, I am being told that each and every metal pool panel must be bonded individually, citing that if the bolts were to come loose or get separated somehow, the entire pool would remain bonded. In addition, I have read and am being told that the bolts securing the bonding lugs to the metal walls must be copper, brass, or stainless steel and the lugs must be listed as direct burial.

References:

The only reference I can find in the 2005 code is Article 680.26 (C)(2) that says the wall of a bolted or welded metal pool shall be permitted as part of the equipotential bonding grid. I cannot find another reference to bolted metal pools anywhere else.

Quustion:

Do the bolted metal walls of the swimming pool not constitute one continuous piece of metal? (Just as the tie wires do on a rebar constructed pool shell.)

(The direct burial, all copper lugs with stainless steel fastening hardware are nearly $5.00 each. If every panel were to be bonded separately, there would be nearly 40 lugs on one pool. The cost of bonding the pool would be more than 25 times what it was and this isn't even close to counting the new 3' equipotential grid.)
 
Ask the inspector where he's finding the wording in the code that requires every bolted section to be bonded individually. This is not the requirement. A ground lug on each section is just as likely (or unlikely) to come loose as the bolts holding the thing together. IMO he is incorrect.
 
It would appear you answered your own question. Those metal side wall assemblies consititute part of the equipotential grid. Same as rebar assembled with tie wires.

Ask the inspector-critter how those lugs are going to loosen inside of cured concrete?
 
That inspector is full of it. Ask him for a code reference. I just did about 7 pools this summer all like the one you described and was never told do that. The only thing that we did do though was if there was a break in the pool walls with say a fiberglass seating unit, we would jump the fiberglass unit with some bond wire around the unit...........man that's unbaleaveable....................where do some of these guys get off?
 
Bonding aluminum pool coping

Bonding aluminum pool coping

I am wiring some polymer wall pools with aluminum coping. The AHJ is requiring me bond each section of coping since they are not tied together mechanically. The problem is that they arr requiring a direct burial lug rated for direct contact with aluminum and for a #8 copper wire. I can not find this type of lug. Does anyone have any ideas how I can bond this coping so it will satisfy the inspector?
 