We had a job where there was substantial stray voltage present in the yard around a pool.
We had bonded the pool ladders, railings, pump, heater, etc as required. But the pool itself was fiberglass, and had no other metal coping, or rebar associated with it.
The problem was the yard was "hot" and the fence next to the propane tank had a significant potential difference due to the bonding grid. We had to install a jumper from the tank to the fence to avoid getting shocked when you walked between the two.
Then, when you got to the gate in the fence, there was a voltage between them. Every time we bonded something else, the voltage difference would move on to the next thing in the yard. It seemed like a never ending battle.