dbuckley
Senior Member
- Location
- Canterbury, New Zealand
I'd go another round with the clamp, testing both wires. If there's a asymetric short, there must be asymetric current - Messers Ohm and Kirchoff never lie...
Randy, can you get a current reading before the breaker trips?i shut the switch off, hook both of them up, turn it on, breaker holds for about 2-3 seconds, pulling 20 amps, and breaker trips.
sounds like there is a metallic path between the lights that is not a path to ground or is a path to the supply EGC, and one or both of the lights has faulted to this metallic path, one with the neutral and one with a hot, so when you hookup both lights it completes the path from neutral to hot?
we know there is not a ground fault because of the GFCI not tripping, so the only other fault would be hot to neutral which the GFCI just passes back to the breaker in the panel.
Long pathway 5.4 ohms in circuit = 22 amps at breaker.
only thing that would make sense to me?
is there any transformers involved with these lights?
Randy, can you get a current reading before the breaker trips?
Or, just try another breaker. Either there really is over 20a, or the breaker trips
Randy, can you get a current reading before the breaker trips?
Or, just try another breaker. Either there really is over 20a, or the breaker trips
ok. service call to a residence.
pool with attached jacuzzi. both have pentair pool lights, 120 vac.
breaker is tripped. when reset, and lamps turned on with switch.
breaker trips. breaker is 20 amp.
GFCI does NOT trip.
i replace GFCI, just for drill. brand new leviton GFCI blank face,
after the light switch. test gfci downstream. it works correctly.
disconnect both lights at their respective junction boxes, and
reset the breaker, and turn the switch on. breaker holds.
gfci holds. premises wiring to box is good.
120 volts at the junction box.
i hook up the first pool light. it goes on, pulls 4 amps. lights up
fine. i disconnect it, and hook up the second pool light. it goes
on as well, pulls 4 amps. lights up fine.
i shut the switch off, hook both of them up, turn it on, breaker
holds for about 2-3 seconds, pulling 20 amps, and breaker trips.
GFCI does NOT trip. at all. ever.
any thoughts on this one?
randy