Re: Swimming Pool..........
Yes I have wired a few pools but most AHJ's here tell us what they want and that's what we try to meet. But it seems that by placing your twist-loc receptacle 6' away will not allow you to have a 3' cord on your pump. That is what is cornfusing. If 680.7(A) and 680.21(A)(5) both require a 3' cord on a pump how can we be in compliance with 680.22(A)(1) with out relocating the pump closer to the receptacle? Yes i've seen it done but and have even done myself, but to give advice out here I would like to be more correct about it.
What I don't understand is why 680.22 requires the receptacle to be 10' away or 5' if all of the 4 items are met. and why if this is for storable pools then why is it under 680.22? and not 680.31?
Yes I have wired a few pools but most AHJ's here tell us what they want and that's what we try to meet. But it seems that by placing your twist-loc receptacle 6' away will not allow you to have a 3' cord on your pump. That is what is cornfusing. If 680.7(A) and 680.21(A)(5) both require a 3' cord on a pump how can we be in compliance with 680.22(A)(1) with out relocating the pump closer to the receptacle? Yes i've seen it done but and have even done myself, but to give advice out here I would like to be more correct about it.