hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
The problem with these types of pools is we tend to think that because there is no electrically supplied equipment around the pool that there is no danger of a shock problem, but we all know that some time in the future someone will eventually even if it is by an extension cord bring a electrically supplied equipment by the pool even if it is for a radio, or at some time later they might want lights added.
Stray voltage is a local event and stray voltage must be brought into the area via a low impedance path, a isolated pool like this would not have a problem of any voltage gradients as long as there is no low impedance path brought to the pool, it would remain at the potential of earth, the myth that a primary line fault a few hundred feet away can cause a voltage to travel through earth is false, most all stray voltage is caused within 25' of the area and its mostly cause by an elevated voltage of grounding conductors from a service that also has an elevated voltage to earth, stick a ground rod into earth and 25' away you will have dropped 100% of the voltage applied to the ground rod and the earth would be back at the potential of earth, of course this depends upon the conductivity of the soil but for most coagulations it works, the higher the resistivity of the soil the larger the sphere of influence around the rod and shells, so a soil with a lower resistivity will have even a smaller shell like 23'.
So we are back to the problem of someone bringing in a conductive path that would cause the stray voltage, who is to say that someone might want to listen to a radio at some future point and run an extension cord out there or at a later time install some lighting, we all know at this time no one will put an EPB system in and someone could be killed, My view is if the pool is intended for people to get in then a EPB system in needed, there is no requirement for it to be connected to the service grounding as this is not the purpose of it.
Stray voltage is a local event and stray voltage must be brought into the area via a low impedance path, a isolated pool like this would not have a problem of any voltage gradients as long as there is no low impedance path brought to the pool, it would remain at the potential of earth, the myth that a primary line fault a few hundred feet away can cause a voltage to travel through earth is false, most all stray voltage is caused within 25' of the area and its mostly cause by an elevated voltage of grounding conductors from a service that also has an elevated voltage to earth, stick a ground rod into earth and 25' away you will have dropped 100% of the voltage applied to the ground rod and the earth would be back at the potential of earth, of course this depends upon the conductivity of the soil but for most coagulations it works, the higher the resistivity of the soil the larger the sphere of influence around the rod and shells, so a soil with a lower resistivity will have even a smaller shell like 23'.
So we are back to the problem of someone bringing in a conductive path that would cause the stray voltage, who is to say that someone might want to listen to a radio at some future point and run an extension cord out there or at a later time install some lighting, we all know at this time no one will put an EPB system in and someone could be killed, My view is if the pool is intended for people to get in then a EPB system in needed, there is no requirement for it to be connected to the service grounding as this is not the purpose of it.