I would like to know if you can run 12/2 UF cable to feed pump motor for pool. (above ground)52" deep.
Inspector wants PVC run with insulated ground wire and exspansion joints on pipe.
Depending on your geographic location in the country, he may be concerned with ground movement from frost heave, such as here in the northeast. [300.5(J)]