Where in the code does it tell me that I must use the same color switch leg as the phase it is on? This came up on A job that the lighting circuits are 277v. Thanks!
210.5 (C) said:Identification for Branch Circuits.
Ungrounded Conductors. Where the premises wiring system has branch circuits supplied from more than one nominal voltage system, each ungrounded conductor of a branch circuit, where accessible, shall be identified by system. The means of identification shall be permitted to be by separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each branch-circuit panelboard or similar branch-circuit distribution equipment.
don_resqcapt19 said:Try 210.5(C)?
Minuteman said:Nope, this just says that different voltage systems shall be identified. Nothing says that a switch with a yellow colored ungrounded 277v conductor on the load can't have a yellow conductor on the line side.
But I wouldn't do it.![]()
RUWired said:According to article 200.7(C)2 this yellow colored ungrounded wire can only be on the line side of the switch.
RUWired said:According to article 200.7(C)2 this yellow colored ungrounded wire can only be on the line side of the switch.
True for now, but not in the 2002 code and likely not in the 2008 code. Under the 2005 code it still has to be identified by system if there is more than one system in the building and given the voltage is very likely that there is more than one system. Unless the method of system identification posted at each panel includes a identification of switch legs, then it would have be the same as what ever was used to identify the system.Don the question was 'do we have to identify the phase of a switch leg'.
210.5(C) only requires identification of the system.
iwire said:I can choose to make all the ungrounded phases of my 208 system violet and all the ungrounded phases of my 480 system pink.
Not saying I would do that, just that the answer to the question asked is no not by the NEC (Right now)
FWIW I thought it odd that the NEC went backward when the removed the identification by phase requiremnt.
In that case, under the 2005 code, the 120 volt switch legs would have to be violet and the 277 volt ones would have to be pink. This would require them to be the same color as the color of the conductor that supplies the switch.I can choose to make all the ungrounded phases of my 208 system violet and all the ungrounded phases of my 480 system pink.
don_resqcapt19 said:Bob,
In that case, under the 2005 code, the 120 volt switch legs would have to be violet and the 277 volt ones would have to be pink. This would require them to be the same color as the color of the conductor that supplies the switch.
Don
don_resqcapt19 said:Bob,
In that case, under the 2005 code, the 120 volt switch legs would have to be violet and the 277 volt ones would have to be pink. This would require them to be the same color as the color of the conductor that supplies the switch.
Don
210.5. There are no exceptions for switch legs.Code reference please.
don_resqcapt19 said:This would require them to be the same color as the color of the conductor that supplies the switch.
210.5 (C) 2005
Where the premise wiring system has branch circuits supplied from more than one nominal voltage system, each ungrounded conductor of a branch circuit, where accessible, shall be identified by system. The means of identification shall be permitted to be separate color coding, marking tape, tagging, or other approved means and shall be permanently posted at each branch-circuit panelboard or similar branch-circuit distribution equipment