Michael,
Don
All ungrounded conductors of each voltage system must be identified as to sytem under the 2005 code. In Bob's example violet was used for the 208/120Y system and pink for the 480/277Y system. If you would use multiple colors to identify each system, then you could have a different color for the switch legs. You would have to post the method of system identification at each panel. You could also use the color to identify the system and some marking as you suggest in your last post to identify the switch legs.Don, where does it say that the identification has to be the same color on both the line & load side of the switch?
Don