Can according to the NEC can you use #14 AWG as a switch leg if the circuit is fed by #12 on a 20 amp circuit?
I don't do it because I was taught so BUT I think it should be, for lighting switch legs/travelers only. As most likely the switch is only 15 amp rated anyhow and is compliant as long as the lighting load doesn't exceed that rating. And especially when dimmers are most commonly rated for only 600-1000 watts anyhow.
Has anyone tried to change it by submitting a proposal?
Ahhhhh come on,
take the word BRANCH and what does that signify. Think of a tree a branch starts out a certain size then reduces as it grows out in different directions.
Why would our our forefathers call it a BRANCH CIRCUIT if it didn't have the ability to be reduced in size determined by its loading ?
I know,
But I have yet to have ever seen any indication of any failure of the 14awg switch leg wires that here too appear to have been commonplace years ago.
I know,
But I have yet to have ever seen any indication of any failure of the 14awg switch leg wires that here too appear to have been commonplace years ago.
Code citation more for the OP. 14ga switchlegs on 20A circuits are not that common here, matter of fact I do not recall the last time I saw one.
Now, poor, overworked, 15A circuits? Dime a dozen here. Pretty much every house built in the 50s here has half the house on one 15A breaker, but mixed 12/14 on a 20 is really rare.
And if your concerned with a short circuit event the 14awg is well capable of opening a 20 amp breaker.
Can according to the NEC can you use #14 AWG as a switch leg if the circuit is fed by #12 on a 20 amp circuit?
According to Nec you are allowed to do it Note that the #14 will become extremely hot. Trying to run to many things on the same line will be hazardous and could cause a nuisance to trigger your cb to power off.Can according to the NEC can you use #14 AWG as a switch leg if the circuit is fed by #12 on a 20 amp circuit?
According to Nec you are allowed to do it Note that the #14 will become extremely hot. Trying to run to many things on the same line will be hazardous and could cause a nuisance to trigger your cb to power off.
According to Nec you are allowed to do it
Reference Please.
Code 2011 table 210.24. 20amp circuit allowed to be 12ga with a 14ga tap
Sent from my iPhone using Tapatalk
also, if I might, I word of caution. Be careful in applying Table 210.24 and note then other Sections mentioned in the actual wording such as 210.19, 210.20. There are some limitations on the Table addressed in those Sections.Code 2011 table 210.24. 20amp circuit allowed to be 12ga with a 14ga tap
Sent from my iPhone using Tapatalk