M mannyb Senior Member Location Florida Occupation Electrician Sep 8, 2022 #1 Customer has GFCI breakers installed at fuel panel for its required switch neutral breaker. Would you say that, other than GFCI purpose, the GFCI does same job as a switch neutral breaker and being used in right application.
Customer has GFCI breakers installed at fuel panel for its required switch neutral breaker. Would you say that, other than GFCI purpose, the GFCI does same job as a switch neutral breaker and being used in right application.
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Sep 8, 2022 #2 No. While the new generation of GFCI receptacles open the neutral, I am not aware of any GFCI breaker that does so.
No. While the new generation of GFCI receptacles open the neutral, I am not aware of any GFCI breaker that does so.
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Sep 8, 2022 #3 No.