Does the N.E.C. specify that the ampere rating of a switch on a branch circuit match the rating of the overcurrent protection of the circuit? If so, where?
But, don't let that make you think you can also use a smaller conductor.mdshunk said:The switch is sized per the controlled load, without regard to the overcurrent protection of the circuit.