switchboard used as a pull box

Status
Not open for further replies.

Stalbott

New member
I have a situation where a switchboard on one system is being used as a pull box for a seperate system. I know there is a code issue with this but I can not find it. Can anyone direct me to the proper code section?

Thanks!!
 

Rockyd

Senior Member
Location
Nevada
Occupation
Retired after 40 years as an electrician.
Since Roger shamed me into dragging my 08 NEC into the house....


I checked the verbage Bob, and it is unchanged -

Exception: Conductors shall be permitted to travel horizontally through vertical sections of switchboards where such conductors are isolated from busbars by a barrier.
 