Designed a project installing a generator to provide backup power for some Telco equipment. I have seen in the past that a lot of times the emergency system is not tested under load since the short transfer interruption causes problems for the loads. I specified a closed transition ATS to eliminate this issue. Now I see where this ATS is being provided with a closed transition, switched neutral. This would seem to indicate I have to consider the gen-set as a separately derived source and provide a bond between the genset neutral and the ground rod system I had installed and taken to the genset. Okay..... but then, if the closed transition during testing occurs will I be creating the potential for transient currents and/or voltages? During a real outage there is no problem, but when testing will this cause trouble? Thanks for your time.