Switched outlet location

Status
Not open for further replies.

Hoodood

Member
Location
nyc
Occupation
Electrical foreman
The prints show a switched outlet for the living room instead of an overhead light. This switched outlet is located across the room from the switch. Is there any code for this switched outlet location? I've always switched the closest outlet to the switch. Thanks
 

FYI, as far as code is concerned, the switch could be across the room. We just put them at entrances because it makes sense.




For that matter the code does not even require the wall switch be in the room it is serving but good luck with that. :)
 
Code issues aside, look at it from a practical perspective. You walk in the room, hit the switch by the door, a floor lamp turns on at the opposite side of the room, and you now have light to safely go into the room. That is what the rule is all about anyway. It doesn't matter whether the light that turns on is on the ceiling or on a table. They just want you to be able to turn on a light.

We have had a discussion or two about what Bob said. A light switch on a wall in the basement that turns on a lamp in an upstairs bedroom meets the code requirement. But recall that the code is not interested in practical designs. It only deals with safety.
 
I've had inspectors make me move the switch near the door that you enter the room in. Was he wrong to require this?
We had to surface mount a box and conduit because it was not accessible.
 
I've had inspectors make me move the switch near the door that you enter the room in. Was he wrong to require this?
Yes, if he was trying to use the NEC as the basis for this requirement. I cannot say what the building codes or local electrical code amendments might have to say on this subject.

(Edited to add: I need to learn how to type faster, or perhaps I should just use my Moderator's Secret Powers to delete Marky's post, so that it looks like this response was entirely my idea. :lol: )

 
Switched receptacles are usually installed in place of fixed lighting to save $$$. The closest receptacle usually gets switched since it only requires a short run of 2-wire for a dead end or a short run of 3-wire if the feed runs through the switch box. Switching a receptacle in another part of the room requires additional material and labor.
 
Split outlet

Split outlet

Ok, so it doesn't matter where in the room the switched outlet is I'm wondering if an outlet is split will that unswitched half still count in the 12ft rule?
 
Ok, so it doesn't matter where in the room the switched outlet is I'm wondering if an outlet is split will that unswitched half still count in the 12ft rule?
6-12 foot rule of 210.52 can include switched outlets, they don't even need to be split wired receptacles, you could switch the entire room's receptacles if you wanted.
 
Ok, so it doesn't matter where in the room the switched outlet is I'm wondering if an outlet is split will that unswitched half still count in the 12ft rule?

Yes, if the entire receptacle is switched it does not count towards the 6'/12' requirement.
 
Yes, if the entire receptacle is switched it does not count towards the 6'/12' requirement.
One can read it at the beginning of 210.52, specifically in 210.52(2), where the switched receptacle(s) become the Lighting Outlet as defined in Article 100.

If only one receptacle on a duplex receptacle yoke is switched, only that one receptacle is the lighting outlet.
 
One can read it at the beginning of 210.52, specifically in 210.52(2), where the switched receptacle(s) become the Lighting Outlet as defined in Article 100.

If only one receptacle on a duplex receptacle yoke is switched, only that one receptacle is the lighting outlet.

Correct and if you switch both as I stated earlier you no longer have the required receptacle to satisfy the 6'/12' rule.
 