Switched Receptacle, 6' rule

Status
Not open for further replies.

jmsbrush

Senior Member
Location
Central Florida
I know in the old days some electricians would switch the whole duplex rec near the door. Now I know in the 2008 if you do that then you need to add another receptacle near the door to meet the requirement of the 6' rule.

So I guess my question is when did this go in effect?
What year code book were you aloud to do this particular install?
 

480sparky

Senior Member
Location
Iowegia
I don't think the NEC has ever differentiated between constant-hot and switched receps in the spacing requirements of 210.52.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The 2008 now requires the receptacles that are used for the 6' and 12' spacing requirements to be constantly energized. A half switched duplex will still satisfy the new requirement and still provide a switched lighting outlet. If I remember correctly a member of this forum is responsible for this change.
 

480sparky

Senior Member
Location
Iowegia
The 2008 now requires the receptacles that are used for the 6' and 12' spacing requirements to be constantly energized. A half switched duplex will still satisfy the new requirement and still provide a switched lighting outlet. If I remember correctly a member of this forum is responsible for this change.

I see it now.... 210.52(2). I was looking in 210.52 (A)..

So the answer to the OPs question is...... 2008! ;)
 

jmsbrush

Senior Member
Location
Central Florida
Well good, because I did that the other day, and I was reading my 2008 NEC hand book, and said" oh no ,I just violated the code!" I might get lucky because, I do not think the county has adopted the 2008 yet!
 