Switches and amperages
South Carolina
I have been told that the difference between a 15A 125V receptacle and a 20A 125V receptacle is only the way that the prongs are laid out. Thus, more than one 15A receptacle can be used on a 20A circuit.
So, what about 15A switches? Is it a violation to use a 15A switch on a 20A circuit?
Also, I was thinking about using a SPDT switch for lighting. The smaller switches are rated for 6A or 10A. The regular toggle switch is more expensive. Thus, I would like to know if I need to spend the extra money to match the Amps or if I could get away with a smaller amperage switch. The load is one closet light.
Thank you for your help.
A 15 amp switch is permitted on a 20 amp circuit. Most standard dimmers are only rated for 600W and they're used on 15 and 20 amp circuits all of the time.
404.14(A).
I think an important thing to emphasize with this is the difference between using something at/below it's rating vs. protecting something with an OCPD at/below it's rating. Many often think the latter is a general rule that applies to pretty much anything, but in fact only applies to a few things (most common example besides conductors is panelboards 408.36). 110.3 applies generally, but that is the former and doesn't specifically require ocpd protection.
Which means that you probably should not use a 15A switch on a 20A circuit if it is feeding a 20A receptacle and you do not know what the eventual load will be.
Yes.
But... this is a closet light, so it would have to be a 2000W light to draw more than 15A and if you have a 2000W light in your closet, you need to rethink what you do in there... 😱
That type of lighting doesn't need to be turned off at all.
Um............ er............... at least................... that's what I've been told. Yeah. That's it. I was told that.
That depends on which stage the plants are in . . . so I've heard. :rolleyes:
To set everyone's mind at peace. I am not planning on putting anything like suggested above in the closet. :) I would like to install a SPDT switch so that I could have the closet light on, off, or set to turn on with the outdoor photo-eye so that the LED closet light would act as a night light. So, probably will be looking at 13W or less. Thankfully, the 6A switch should be able to take that. :)
Thanks for your help.