poweringtech
Member
What part of the code that says, switches should switch off all ungrounded conductors? What type of snap switch should be used in a line-to-line system voltage? 
You will have to be more specific about the switch application.line-to-line system voltage?
There is no general provision stating a switch must open all ungrounded conductors, therefore there is no a need for an exception.Originally posted by poweringtech:
Iwire,
What application in the code that does not require to open all ungrounded conductor
Originally posted by poweringtech:
However for article 430.84, Where it says Need Not Open All Conductors.
The controller shall not be required to open all conductors to the motor.
Isn't the code referring to the grounded conductor but not to the ungrounded conductors?
[ November 21, 2004, 10:02 AM: Message edited by: iwire ]
That is 100% correct in many applications.Originally posted by poweringtech:
Charlie says that you dont have to switch off all ungrounded conductor if you are using the switch only as a control.
This means that even if two conductor are hot, the code allows that you can only switch even one of the two hot conductors?
In the case of a lamp socket 410.48 requires the switch to disconnect all the ungrounded conductorsOriginally posted by poweringtech:
While kiloamp says that if the load is supplied by 2 hot conductors the light switch should always be 2pole.
If it is an ballasted type fixture that uses two ungrounded conductors 410.54(B) applies.410.48 Double-Pole Switched Lampholders.
Where supplied by the ungrounded conductors of a circuit, the switching device of lampholders of the switched type shall simultaneously disconnect both conductors of the circuit.
410.54(B) Switching. Where supplied by the ungrounded conductors of a circuit, the switching device of auxiliary equipment shall simultaneously disconnect all conductors.
What kind of fixture?Originally posted by poweringtech:
I have one of my electrician nearly electrocuted while changing the fixture,
I am not trying to pass the buck however your maintenance personnel bare responsibility for their own safety.Originally posted by poweringtech:
there could be a danger of electrocution if for example the light is being replaced and one of the hot conductor is not switched off.Can be a code suggestion wherein if the switch will not open all ungrounded conductors because it is only being used for control, it should be properly marked that it is not a disconnect or for control only.
So that maintenance personnel will not be misled by the switch as the same as the disconnect to prevent accident