switches in patient rooms

Status
Not open for further replies.

sam34

Member
Location
Missouri
Hello every one,

Does light switches in exam rooms are required to have metal raceway system or AC cable (per section 517.13(A)? I have an inspector that told us since there is no such a thing called hospital grade switches, all switches for patient area's needs to be from the outside. Any Ideas?
 
Re: switches in patient rooms

517.13(A) says...all branch circuits serving patient care areas shall be provided... I believe that means the lighting circuit serving the exam room must comply, but a metal faceplate is exempt per (B) Exc. #1. If this is an exam room in an outpatient clinic, for example, the NEC doesn't require hospital grade receptacles, and that should be moot. I regularly specify spec grade receptacles and switches in clinics, etc.
Jim T
 
Re: switches in patient rooms

Thank you Jim for replying, This place is in shopping Mall where they have a room for hearing testing which they will consider an exam room. So are you saying that I don't even have to have hospital grade receptacles?

Thank you
 
Re: switches in patient rooms

Sam,

That is correct. You do not need healthcare grade receptacles in the location you are speaking about.
-Ed
 
Re: switches in patient rooms

look at 517.13 (B) exception no. 2, and the
definition of patient vicinity.
 
Re: switches in patient rooms

Sam34, although the area you describe is a far stretch of the imagination as too being a healthcare facility, you can go to this page on Patient Vicinity Grounding and notice the light switch beside the "Patient Bed" in the first graphic.

Roger

[ January 21, 2005, 09:43 PM: Message edited by: roger ]
 