hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
NEC 2017 408 part II says switchgear and switchboard and 408 part III is about panelboard.
Part III 408.36 exception allows MLO panelboard does not have to have individual protection for panelboard if its service equipment multiple disconnects 230.71.
Also note part III 408.36 first paragraph says if panelboard is not service equipment then overcurrent protection shall be provided not greater than rating of Panelboard
Where is all the above for switchboard and switchgear 408 part III?
Questions:
1. Does this mean that switchgear that is NOT service equipment can be provided by breaker higher than its rating? For example MLO switchgear NOT service equipment is 1000A bus but up stream breaker can be 1200A trip? If no then I don’t see it in 408 part II?
2. Does this mean that switchgear that IS service equipment is exempt or not like panelboard is for 408 part III 408.36? If it is then where is it in 408 part III or is it somewhere else in NEC 2017?
Part III 408.36 exception allows MLO panelboard does not have to have individual protection for panelboard if its service equipment multiple disconnects 230.71.
Also note part III 408.36 first paragraph says if panelboard is not service equipment then overcurrent protection shall be provided not greater than rating of Panelboard
Where is all the above for switchboard and switchgear 408 part III?
Questions:
1. Does this mean that switchgear that is NOT service equipment can be provided by breaker higher than its rating? For example MLO switchgear NOT service equipment is 1000A bus but up stream breaker can be 1200A trip? If no then I don’t see it in 408 part II?
2. Does this mean that switchgear that IS service equipment is exempt or not like panelboard is for 408 part III 408.36? If it is then where is it in 408 part III or is it somewhere else in NEC 2017?