How about max height for OCPD?
240.24 Location in or on Premises.
(A) Accessibility. Overcurrent devices shall be readily accessible
and shall be installed so that the center of the grip
of the operating handle of the switch or circuit breaker,
when in its highest position, is not more than 2.0 m (6 ft
7 in.) above the floor or working platform, unless one of the
following applies:
(1) For busways, as provided in 368.17(C).
368.17(C) Feeder or Branch Circuits. Where a busway is used
as a feeder, devices or plug-in connections for tapping off
feeder or branch circuits from the busway shall contain the
overcurrent devices required for the protection of the feeder
or branch circuits. The plug-in device shall consist of an
externally operable circuit breaker or an externally operable
fusible switch. Where such devices are mounted out of
reach and contain disconnecting means, suitable means
such as ropes, chains, or sticks shall be provided for operating
the disconnecting means from the floor.
They also take the service at 13.8kv own their own high voltage service disconnect, pad mount transformer sized per the NEC, exterior mounted temp generator connections in case the locomotive sized one on site goes down.
Does the generator run all the loads, select loads or just NEC mandated life safety?
Not 100% of the loads but darn close to it.
This is insane! The foreman's brain must have look like a thousand pounds of tangled up spaghetti by the end.
I'm unfamiliar with the copper gas line running into the top of the panels.?
Sent from my iPhone using Tapatalk
very nice work, Why don't companies rent benders instead of buying everything prefab? Is the pipe too expensive if you mess up?
I'm curious about the MI cable. What's it for?
Whoops, I missed the second page. Never mind.
My understanding (I could be wrong) is that MI is capable or surviving a fire to some degree or another. I have to admit its really unique for a basic building. I've seen the single line for some large high rise buildings and even they don't use MI, which imo is one place that should mandate it.
:thumbsup:
That entire building would fit in their bakery.
My wife wont shop there because it is too big.
The company owns a number of benders, I was not on this site during construction so I can't say why factory bends where chosen over the field made but no one but an electrician would care about it.![]()