Switchgear vs. MCC

Merry Christmas
Status
Not open for further replies.

MD88

Member
Hello,

I'm trying to figure out the best way (cheapest, while still safe) to do the following thing:

I have 5kV coming in to a room, and I need 1 5kV motor starter and a 4160/480V transformer for other loads. Now, the classic way to do this is to get 5kV switchgear, feeding the transformer and the starter. So I'd need an main breaker and 2 feeder breakers in the switchgear, plus an MCC with a 5kV starter.

But I was thinking, what about having the 5kV feed right into a 5kV MCC with a main breaker, 1 starter and a feeder to the transformer. It seems like it'd be quite a bit cheaper, take up less room and work just fine! I have a feeling there must be a reason why this wouldn't work, but please explain! Thanks
 
5 kV MCC as Switchgear

5 kV MCC as Switchgear

That's a common way of doing it.

Use a latched contactor to feed the transformer. It is the same as a motor starter but it is mechanically latched so it doesn't drop out on loss of power. The fuses protect for short circuits, a relay trips the contactor to provide overload and ground fault protection. Note that you are not using a motor starter to feed a transformer even though they look almost identical and have the same parts.

Depending on your load, you may be able to use a fused disconnect switch for the incoming main breaker or even an 800A latched contactor.

If you want to really cut costs, use the feeder breaker back at the 5 kV switchgear as the main. You can run a close and trip circuit from the room back to trip the feeder breaker if someone wants control in teh room. Lockout is a little more complicated because the electricain has to walk back to the gear to place the lock, but it is still safe.
 