I have a 1600Amp 480/277V switchgear the plant manager decided to put an enclosure around
The space in front is 38 1/2", the space on 1 side is 31 1/2", space on other side is 10" amount no working space behind the gear due to building steel, walls are foam filled metal skinned "sips panels" and no exposed live parts.
I have been looking over 110.26 (C) (2) and not sure if this would qualify for 2 doors or 1, and am looking for feedback.
Thanks
	
		
			
		
		
	
				