Re: Switching neutral in a transfer switch
We keep tripping over the wording on separately derived systems. What Bennie and others keep arguing is that there should be no conductive pathway between the two systems. My ongoing problem is that no matter how well they argue for that approach the US NEC does not permit it.
What I want is an answer to how I could possibly build an isolated electrical system in any building that is served by utility power.
If I use bennies solution of putting the transfer switch ahead of the service disconnect I have to have a service rated transfer switch. So I do the connection of the main bonding jumper to the neutral on the load side of the switch. If I make the connection on the load side have I not violated the provision of 250.24(A)(1) and 250.24(B).
250.24 Grounding Service-Supplied Alternating-Current Systems.
(A) System Grounding Connections. A premises wiring system supplied by a grounded ac service shall have a grounding electrode conductor connected to the grounded service conductor, at each service, in accordance with 250.24(A)(1) through (A)(5).
(1) General. The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.
(B) Grounded Conductor Brought to Service Equipment. Where an ac system operating at less than 1000 volts is grounded at any point, the grounded conductor(s) shall be run to each service disconnecting means and shall be bonded to each disconnecting means enclosure. The grounded conductor(s) shall be installed in accordance with 250.24(B)(1) through (B)(3).
I don't see anything in the code that would permit me to unbond the utility's grounded conductor from the enclosure of the service disconnecting means regardless of whether that enclosure is the transfer switch cabinet or another cabinet.
If anyone can find a way that is code compliant to interrupt the inevitable conductive path of all code compliant installations there would be a use for such techniques on every livestock ranch or farm. The problem is that it is not in the utilities' interest to permit us to disconnect there neutral from the premises grounding electrode as they are using the earth as a parallel conductor for their neutral.
--
Tom
[ March 29, 2003, 02:55 PM: Message edited by: hornetd ]