Switching neutrals or not

Status
Not open for further replies.

Dbarrett

Member
Location
Reno, NV
I know this has already been brought up in the past but how do you guys feel about switching Neutrals in the knifeswitch? I don’t see it necessary but I did find that 690.15(d)
It states: Equipment Disconnecting Means. An equipment disconnecting means shall simultaneously disconnect all current- carrying conductors that are not solidly grounded. I know that 404.2(b) states otherwise. Thoughts?


Sent from my iPhone using Tapatalk
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I know this has already been brought up in the past but how do you guys feel about switching Neutrals in the knifeswitch? I don’t see it necessary but I did find that 690.15(d)
It states: Equipment Disconnecting Means. An equipment disconnecting means shall simultaneously disconnect all current- carrying conductors that are not solidly grounded. I know that 404.2(b) states otherwise. Thoughts?


Sent from my iPhone using Tapatalk
Read them again; they say the same thing. Don't switch the neutral.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
The neutral isn’t a current carrying conductor?


Sent from my iPhone using Tapatalk

..."disconnect all current- carrying conductors that are not solidly grounded."

It's solidly grounded.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
And if it is a fusible switch you can not switch the neutral anyway. While in some cases the code requires switching a grounded conductor, is very rare and there could not be a fuse.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The neutral may be switched, as long as all non-grounded conductors are simultaneously opened, but may not be individually fused.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The neutral may be switched, as long as all non-grounded conductors are simultaneously opened, but may not be individually fused.
And in certain cases, like a transfer switch from a service to a non-SDS generator installation, the neutral must be switched along with the hot conductors. Such transfer switches often incorporate a time offset so that the neutral is broken after the hot conductors and makes the new connection before the new hot conductors are switched in. This avoids even momentary operation of MWBCs with an open neutral.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
For a run-of-the-mill AC side disconnect for a solar inverter, there is no reason whatsoever to switch the neutral, and it's generally prohibited.
 

Dbarrett

Member
Location
Reno, NV
I agree that it shouldn’t be disconnected, it’s just how my company chooses to install things. Just wanted to get a majority feedback. Why prohibited?


Sent from my iPhone using Tapatalk
 

pv_n00b

Senior Member
Location
CA, USA
I agree that it shouldn’t be disconnected, it’s just how my company chooses to install things. Just wanted to get a majority feedback. Why prohibited?

You don't want to create an ungrounded system where the NEC requires system grounding. For grid-tied inverters that shut down when disconnected, this is not an issue. If you have a multimode inverter that continues to provide power after being disconnected then an alternate way to ground the grounded conductor would be needed if it was disconnected from the bond in the service entrance.
 
Status
Not open for further replies.
Top