switching power factor on withe a standby generator

Status
Not open for further replies.
Location
abudhabi
is it ok to switch on power factor correction capacitor pannel with the facility's stand by generators ?? i heard that it rises up generator voltage and may cause possibile generator damage?? please advise.
 
is it ok to switch on power factor correction capacitor pannel with the facility's stand by generators ?? i heard that it rises up generator voltage and may cause possibile generator damage?? please advise.
You do not want to use a compromise set of PF correction capacitors which sometimes over corrects and leaves a PF less than 1 but capacitive.
Some regulators do not cope well with a capacitive load.
A perfectly resistive load should be just fine.
 
is it ok to switch on power factor correction capacitor pannel with the facility's stand by generators ?? i heard that it rises up generator voltage and may cause possibile generator damage?? please advise.
Yes. If you over correct it is likely to increase the voltage.
 