Switching question

Status
Not open for further replies.

FrancisDoody

Senior Member
Location
Durham, CT
I have to install exhaust ventilation into three shower/changing stalls at one of the local swim club. The stalls each have lighting via a timer switch. All three are on the same branch circuit. I would like to energize the fan as soon as the lights go on. The ceiling is open above. Could this be controlled by a line voltage relay like a RIB. How would you do it. Thanks.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You could use one relay for each time switch. Wire the three relays N/O contacts in parallel to feed the fan. Any one time switch will close its relay and turn the fan on.
 