Are these precise freq sets? They have fuel control for both? Meaning they have an actuator controling the fuel rates to maintain
PRECISE hz....
On top of Hz being correct. You may have some other problems getting them to completely share a load equally. You are using a transformer for one since they are not the same voltage, is the transformer and 2500v generator rated for near the same kw? The kw, voltage and Hz are sensed on one unit before the transformer? If so there will be some lag after the transformer....
If there is a difference in size, slight difference in Hz, or voltage output it may be difficult to get them to share a load EQUALY. The transfer switch may sense this slight variance in voltage and
correctly not transfer over. It should only do so when there is ZERO voltage between them through complete cycles. With both generators on, one leading or lagging there will be current between them, and thus not a clean wave form to match the utility - you might not ever get ZERO through a complete cycle. On less complicated low and med voltage gen sets there would be a set of lights between them - when the lights were off - it would be safe to connect them - those lights kind of have a mesmerizing effect as they cycle in and out of phase from each other. If the lights are on - there is a voltage difference. More modern gen sets made to be paralleled, and transfer switches do the same thing waiting for there to be no voltage - they just do it without the fancy old fashioned light bulbs......
And the idea that if they are parallel then the Hz is a dead on match match is a little off base, one may lead or lag, and still be able to function, but never be precise. There will be current and therefore a voltage difference between them at certain points of the cycle. If one is a few degrees off from the other you'll just get some current between them, if off 20-120 or 180 then you have a problem with the OCP tripping - hopefully.... If already linked they will hold each other to a certain degree,
but not precisely. As a combined output it will be a broader sine wave than normal. Since you transfer switch is looking for ZERO at peak, and quite possibly between cycles it may never find it....
I suggest finding
a safe method of sensing voltage, current, current direction +/or kw, and Hz after the transformer of the 480 set - and you may have a chance????? Since you are really paralleling a generator, and a transformer IMO - base operation of the 480 set on the output of the transformer itself.
FYI - I would not be so worried about standing next to the gen sets - assuming there is good OCP, stay away from that transformer though - there is an electrical arm wrestling match going on inside it that you want no part of.... Most transformers are not designed to parallel two sources through - check with the manufacturer and do thermal testing to see if it is getting too hot IMO.
Also see my responce to coulters well versed post (and I mean that...) in the other thread on post
#26