Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
NEC 250.30 A1 a system bonding jumper shall be made at any point of the separately derived system from the source to the first disconnecting means OR IT SHALL BE MADE AT THE SOURCE OF A SEPARATELY DERIVED SYSTEM THAT HAS NO DISCONNECTING MEANS OR OVERCURRENT DEVICE
what is meant by “no overcurrent protection or disconnecting means?” A separately derived transformer system must have over current at the primary source windings or both primary and secondary windings so this statement makes no sense unless they mean only secondary conductors?
And I’m not sure what they mean about not having a disconnect do they mean disconnect upstream of transformer or below as in the distribution panel? The code apparently leaves this to interpretation?
Also separately derived systems located outdoors away from structure requires a grounding electrode conductor installation at the outdoor source? Doesn’t this grounding electrode connection at the outdoor separately derived outdoor system force the system bonding jumper to be also located at outdoor source? Thanks
what is meant by “no overcurrent protection or disconnecting means?” A separately derived transformer system must have over current at the primary source windings or both primary and secondary windings so this statement makes no sense unless they mean only secondary conductors?
And I’m not sure what they mean about not having a disconnect do they mean disconnect upstream of transformer or below as in the distribution panel? The code apparently leaves this to interpretation?
Also separately derived systems located outdoors away from structure requires a grounding electrode conductor installation at the outdoor source? Doesn’t this grounding electrode connection at the outdoor separately derived outdoor system force the system bonding jumper to be also located at outdoor source? Thanks