DARUSA
- New York City
But the EBJ on the load size of the disconnect will be sized base on the table 250.122 or I'm wrong.?
I do not see a conduit as meeting the requirements of 250.102(A). I do agree that 250.30(A)(2) implies the use of something other than a wire conductor as the equipment bonding jumper. It doesn't tell us what else can be used, so we jump to 250.102(A) to find that information.
What good does a grounding conductor bonding the transformer enclosure to the system disconnecting means serve anyway? Couple that with the fact the transformer enclosure is required to be grounded to the primary supply.Don, I can see what you are saying, but 250.102(A) says a bonding jumper shall be a wire, bus, screw, or similar suitable conductor, could a metallic raceway not be a suitable conductor?
For what it is worth I have always used a wire for an equipment bonding jumper on the secondary of a transformer.
Chris
What good does the primary EGC do for a secondary side fault? The equipment bonding jumper on the secondary side bonds the transformer enclosure to the secondary grounded conductor via the line side bonding jumper.What good does a grounding conductor bonding the transformer enclosure to the system disconnecting means serve anyway? Couple that with the fact the transformer enclosure is required to be grounded to the primary supply.
With a transformer installed per the NEC, I would expect that a secondary ground fault on the line side of the secondary OCPD would cause the primary OCPD to open.
With just a primary grounding/bonding connection to the transformer, the impedance of that fault path back to XO may be high enough to prevent the primary OCPD from quickly clearing the secondary ground fault.
Mark,...
In addition, if the system is wired as such, having the SBJ being installed at the disconnect and not having a jumper from XO to the transformer's frame, how exactly would a secondary fault to ground (Metallic raceway for example), line side of the sec ocp, behave and what path would the fault take? Would it flow back to the primary's transformer? If so, that confuses me somewhat as the secondary system would be from a separately derived source. Electricity tries to get back to it's source but in the example above, how can the sec fault accomplish this w/out the XO being bonded to the transformer? Don, you described what I'm trying to grasp, perhaps you could dumb it down for me a little.
For the record, I agree with Don. I assumed the role of devil's advocate to pose the question... and he nailed itThis is an interesting topic/debate. Smart and Don are legendary members here and they seem to disagree on something...
If the only path is via the earth between the two grounding electrodes, it would be very rare to have a low impedance path.T... Would the fault flow back to the primary's GEC and in turn seek to get to the secondary's GEC which may or may not be a low impedance path?
IMO, with emphasis, yes.OK, so we can agree that installing the SBJ at the trans and running the GEC from there is a better design than installing the SBJ (And GEC) at the disconnect or panel?