please see attached image. both transformers are pad mount. as of now i am assuming the utility is grounding their transformer as shown. I am not sure what standard practice is. assuming they do would their be any issues with the grounding as shown on the step up transformer?

my primary concern is the removable bonding strap that comes pre-installed on the transformer as shown. if it is left on will there be any current between the ground rods through the ground? i can't convince myself if there is a complete circuit with voltage or not. a grounded conductor will not be connected between the two transformers.
 

Attachments

  • IMG_20170228_161952555.jpg
    IMG_20170228_161952555.jpg
    134.5 KB · Views: 6

Smart $

Esteemed Member
Location
Ohio
Remove the bonding strap connected to PRI X2 in the step up transformer. Connect it to SEC H2 along with the secondary grounded conductor (currently depicted as connected to enclosure on right side).

BTW, the secondary is simply a single voltage, assuming 4160V. It is definitely not 4160GY/2400, as this would be a 3Ø wye configuration.
 
Last edited:

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Remove the bonding strap connected to PRI X2 in the step up transformer.

Absolutely.

In the 3-phase wye transformer the voltage L-G is 277V. While, the single phase transformer primary winding arrangement the voltage L-G is only 240V.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Absolutely.

In the 3-phase wye transformer the voltage L-G is 277V. While, the single phase transformer primary winding arrangement the voltage L-G is only 240V.

And the above voltage difference implies that the neutral of the wye is at about 138V relative to the neutral of the single phase coil. You will either see high current or high voltage between the two 'grounds'.

-Jon
 
Smart$ said:
BTW, the secondary is simply a single voltage, assuming 4160V. It is definitely not 4160GY/2400, as this would be a 3Ø wye configuration.

Note that is how these single phase transformers are typically designated. The transformer high side is 2400, line to neutral of a 4160 wye system.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
As drawn there is no neutral. So unless the OP depicts it incorrectly, Smart$ is right (as usual).
Many of those transformers are a single bushing on one side of the HV coil and bonded to the case on the other, so at very least we can call it a grounded conductor whether it is a true neutral or not.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Many of those transformers are a single bushing on one side of the HV coil and bonded to the case on the other, so at very least we can call it a grounded conductor whether it is a true neutral or not.

Unless I am mistaking what is being said or terminology, it would be a grounded conductor, but not a neutral and the reason is exactly why the code uses the terms the way they do. A neutral would have to be a tap point in the center of the transformer coil as drawn. I don't see how it could be referenced as dual voltage when there is not a center tap. if this is just a habit which it seems like electrofan and smart$ are saying then it is a bad habit. This is all dependent on whether I actually understand what smart$ was saying which is very possibly a false assumption.:)
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Unless I am mistaking what is being said or terminology, it would be a grounded conductor, but not a neutral and the reason is exactly why the code uses the terms the way they do. A neutral would have to be a tap point in the center of the transformer coil as drawn. I don't see how it could be referenced as dual voltage when there is not a center tap. if this is just a habit which it seems like electrofan and smart$ are saying then it is a bad habit. This is all dependent on whether I actually understand what smart$ was saying which is very possibly a false assumption.:)
You see this often on POCO transformers, 2400/4160 rating on a single phase two terminal unit (one terminal may effectively be the case). I don't know why they do that, bottom line is the unit has a 2400 volt rated coil on the high volt side.
 

robeward

Member
Location
raleigh
Wow! Thanks for all the replies. It seems to be confirmed that the bonding strap should be removed for this setup. That was my conclusion but I just wanted to get some opinions.

I think everything posted is spot on.

I've never seen a set up like this.
I did go to Duke Energy
https://www.duke-energy.com/_/media/pdfs/partner-with-us/service-requirements-manual.pdf?la=en
Pages 85, 86, 87.

This isn't for a NC installation but I still will read through this.

And the above voltage difference implies that the neutral of the wye is at about 138V relative to the neutral of the single phase coil. You will either see high current or high voltage between the two 'grounds'.

-Jon

I am trying to sort out system grounding rules and the implications of an incorrect installation, or in this case if we hadn't thought about removing the strap that comes standard from factory. You are basically saying a ground fault would have been created between the two transformers and some amount of current would circulate between the transformers? The amount of current would mostly depend on resistance in the earth connection?

Electrofelon is correct if the OP is reverse wiring a typical pole pot. It's just how MV equipment is designated.

Correct. Reverse wiring this one. Just how they are designated. I believe there is an ANSI standard governing this designation.

Many of those transformers are a single bushing on one side of the HV coil and bonded to the case on the other, so at very least we can call it a grounded conductor whether it is a true neutral or not.

Correct. If ordered with the 4160GY/2400 designation, one side of the HV coil is bonded to case by factory, internally. This means you could use a bank of three of these to develop a three phase service.

Please see attached pictures of step up transformer with bonding strap.
 

Attachments

  • xfmr.jpg
    xfmr.jpg
    111.1 KB · Views: 2
  • plate.jpg
    plate.jpg
    95.3 KB · Views: 2

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Note that is how these single phase transformers are typically designated. The transformer high side is 2400, line to neutral of a 4160 wye system.

Typically a single phase utility system with a G/ in its voltage, like 4160G/2400, means that the utility system is 4160 L-L and 2400V L-G it does not necessarily say the circuit is 3-phase or 1-phase.
As I remember, it does tell the 'line workers' that a single phase transformer winding with one insulated terminal and 1 grounded terminal will be 2400V while a single phase transformer with (2) insulated terminals would be 4160V.
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
And the above voltage difference implies that the neutral of the wye is at about 138V relative to the neutral of the single phase coil. You will either see high current or high voltage between the two 'grounds'.

-Jon
I am trying to sort out system grounding rules and the implications of an incorrect installation, or in this case if we hadn't thought about removing the strap that comes standard from factory. You are basically saying a ground fault would have been created between the two transformers and some amount of current would circulate between the transformers? The amount of current would mostly depend on resistance in the earth connection?

Essentially yes. If you put a meter between the neutral of the wye and the center point of the single phase transformer, you would measure a pretty stiff 138V. Connecting these two points would cause large circulating currents in the transformer(s), and if you ground these two points the current flow would depend on the ground electrode resistance.

My assumption is that the single phase transformer is most commonly used for step down operation, where the secondary is supposed to be grounded by the strap...but when this transformer is used for step up operation the strap needs to be removed.

-Jon
 
As I remember, it does tell the 'line workers' that a single phase transformer winding with one insulated terminal and 1 grounded terminal will be 2400V while a single phase transformer with (2) insulated terminals would be 4160V.

Jim, if you are saying that a two bushing transformer designated 4160y/2400 takes 4160, that is not the case. I thought that was the case myself and started a thread on that topic last fall. These "utility type" designations are silly imo.

The op needs to be careful in getting the correct number if bushings and the correct voltage. As drawn and designated, he would have 2400 not 4160.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
You see this often on POCO transformers, 2400/4160 rating on a single phase two terminal unit (one terminal may effectively be the case). I don't know why they do that, bottom line is the unit has a 2400 volt rated coil on the high volt side.

Ahhhhh!:thumbsup:
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
I am trying to sort out system grounding rules and the implications of an incorrect installation, or in this case if we hadn't thought about removing the strap that comes standard from factory. You are basically saying a ground fault would have been created between the two transformers and some amount of current would circulate between the transformers? The amount of current would mostly depend on resistance in the earth connection?

There are several things that can happen many of them are a threat to life. First remember the basis of current flow. Current takes the path of least resistance. Draw out the circuit with the primary coil of the transformer, the center tap and the source. You will see that current can basically flow two ways. From L1 through the coil and back to L2 or from either L1 or L2 through half the coil and back along the ground through the bonding point of the neutral and the ground and the along the neutral to the source.

Remember that the ground is not allowed to intentionally carry current with VERY few exceptions in the code. Anything that causes a higher impedance in one side (half) of the the transformer coil will cause some current flow on the ground. A fault (open) on either L1 or L2 will cause current flow on the ground that is equal to the current on the line wire. Now picture the ground being insufficient, (loose connection, broken ground wire. All exposed metal between the point where one failed to remove the strap and the break point would be sitting there waiting for a person to complete the circuit to another grounding point.

I am putting this is simple concepts. One could delve quite a bit deeper in to it with exceptions additional problems, etc. But it is far more than having current travelling between the transformers. (btw, that would also technically be "between coils")
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Jim, if you are saying that a two bushing transformer designated 4160y/2400 takes 4160, that is not the case.

You are correct, the simple presence of two bushings does not necessarily indicate the voltage.

The terminology used by POCOs, and the equipment manufacturers focused on them, is not always directly interchangeable with the terminology of the NEC, and the premises wiring industry.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
You are correct, the simple presence of two bushings does not necessarily indicate the voltage.

The terminology used by POCOs, and the equipment manufacturers focused on them, is not always directly interchangeable with the terminology of the NEC, and the premises wiring industry.

So would it be fair to say that the utility designation of 4160/2400 is just indicating that it can be used with either a single ended 2400 source or with a 4160Y/2400 source as long as in either case it is connected across a 2400V potential?
In the second case that would require an L-N connection to the wye source.
If the transformer has two insulated primary bushings, it could also be connected line to line IF the line to line voltage is 2400.
 