Joethemechanic
Senior Member
- Location
- Hazleton Pa
- Occupation
- Electro-Mechanical Technician. Industrial machinery
That's interesting.Drive would not run until I disconnected capacitors.
That's interesting.Drive would not run until I disconnected capacitors.
Less current also means lower IR loss in cable.See the beer picture. The less foam, the smaller a glass needed to deliver the desired amount of beer.
If you improve power factor, you need less current to deliver the same power at a given voltage. Less current means smaller cables or lower cable loss.
Jon
In your last sentence, do you know why the VFD does not run?In my area the ultility company would charge commercial customers a surcharge if power factor was below 90% . We had to add capacitor banks at several locations. Now with everybody using LED every where you have to watch their power factor. They usually do not list PF on spec sheet or boxes but have seen it as low as 80%. Hope the government make LED manufacturers only produce LED lamps & luminares with a PF of at least 95%. Never install PF capacitors on output side of any VFD'S. We had a contractor install two 30 HP drives on 40 year old air handlers that each motor had a PF capacitor. Drive would not run until I disconnected capacitors.
Feeding power to a capacitive load would certainly be different than the expected inductive.In your last sentence, do you know why the VFD does not run?
Variable speed drives and power factor caps are not comparable. Displacement and distortion factors are different quite things.In my area the ultility company would charge commercial customers a surcharge if power factor was below 90% . We had to add capacitor banks at several locations. Now with everybody using LED every where you have to watch their power factor. They usually do not list PF on spec sheet or boxes but have seen it as low as 80%. Hope the government make LED manufacturers only produce LED lamps & luminares with a PF of at least 95%. Never install PF capacitors on output side of any VFD'S. We had a contractor install two 30 HP drives on 40 year old air handlers that each motor had a PF capacitor. Drive would not run until I disconnected capacitors.
To the pulsed transistors in the output of the VFD, the capacitor charging current looks no different than a short circuit. So a good VFD will detect that and protect itself by disabling the transistors, using what’s called a “base block” that immediately opens the circuit to the base emitters. A cheap VFD might just destroy itself. There’s also a risk of damaging the capacitors. Some of the times I have seen this scenario, the results have been catastrophic. They were lucky if all it did was disable the drive…Feeding power to a capacitive load would certainly be different than the expected inductive.