I don't think that you can install this product and be in compliance with the rules in 400.8. Others see it as compliant.
If you want an outlet out on a large deck, away from any walls, this would work out really well. Especially if the railing is glass or SS cable.
You could try that, but it would get a red tag from me.400.7(A)9
You could try that, but it would get a red tag from me.
There is no requirement that the AHJ accept the listing, and just because it is listed, does not mean the installation of the product would not be a code violation.ad.UL.listed
There is no requirement that the AHJ accept the listing,
IMO, it doesn't violate 400.8(1) because its not "fixed" wiring.
It's hard to say exactly what they meant by "fixed", but the cord moves to allow the cover to open, so I would call that the opposite of fixed.
Also, looking at the instructions, the cord is also not "fixed" to the structure at any point. It's only connected on each end.
I see the cord as being a substitute for fixed wiring. That is wiring that is installed per one of the Chapter 3 wiring methods.400.8(1) As a substitute for the fixed wiring of a structure
So, in you area, is it acceptable to have a cord and plug connected device above a drop ceiling as long as the device is listed?For Jay and I there is.
So, in you area, is it acceptable to have a cord and plug connected device above a drop ceiling as long as the device is listed?
Plus $100 for the inspector. (For the re-inspection visit after you educate him, of course.)$126.90/ea!
Plus $100 for the inspector. (For the re-inspection visit after you educate him, of course.)
The rule in MA is the inspector of wires must accept listed equipment when it is installed per its listing.